Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

Embed Size (px)

Citation preview

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    1/31

    Presentation to Artificial Lift ForumNovember 2011

    UL 1741 Distributed Generation Standard

    Ronald A. Dombrowski,

    Vice President, CCW

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    2/31

    What is UL1741 and why should I care?

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    3/31

    UL 1741 is the standard that inverter-basedgenerators must meet to put electricity on the

    grid

    and get paid for it.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    4/31

    You should care about UL1741 because up to40% of the energy you are putting into yourbeam pumps may be recovered with aregenerative drive system.

    With a UL 1741 certified system, that can comright off your electric bill.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    5/31

    You should care about UL1741 because up to40% of the energy you are putting into yourbeam pumps may be recovered with aregenerative drive system.

    With a UL 1741 certified system, that can comright off your electric bill.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    6/31

    Distributed Generation in TEXAS

    Distributed Generation:An electrical generating facility located at acustomer's point of delivery (point of commoncoupling) of ten megawatts (MW) or less and

    connected at a voltage less than 60 kilovolts (kVwhich may be connected in parallel operation tothe utility system.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    7/31

    Distributed Generation in TEXAS (cont)

    The Public Utility Commission of Texas (PUCTencourages the use of distributed resources.

    Texas Public Utility Regulatory Act (PURA) of1999 includes customer rights and safeguards

    Section 39.101(b)(3) of PURA states A

    customer is entitled to have access . . . to on-sdistributed generation . . .

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    8/31

    Distributed Generation in TEXAS (cont)

    The PUCT established Substantive Rules forinterconnecting distributed generation.

    Substantive Rules Sections 25.211 and 25.212 addres Technical Aspects

    Procedural Aspects

    for interconnection of distributed generation.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    9/31

    Distributed Generation in TEXAS (cont)

    The PUCT established Safety Requirements forinterconnecting distributed generation.

    Safety Requirements ensure DG is designed and

    installed in a way that: is not a safety hazard to utility personnel, equipment or other

    customers

    Does not disturb other customers or degrade quality ofdistribution system

    Provides reliable service to DG owner and utility

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    10/31

    Distributed Generation in TEXAS (cont)

    UL 1741 forms a part of the Safety Requirements

    Virtually all Texas utilities require compliance with UL

    1741 standards

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    11/31

    Distributed Generation in NEW MEXICO

    17.9.568.8 APPLICABLE CODES AND STANDARDS:B. In order to qualify for any interconnection procedur

    each generating facility generator shall be inconformance with the following codes and standard

    as applicable:(3) UL 1741 Inverters, converters and controllers for u

    in independent power systems or equivalent.

    TITLE 17 PUBLIC UTILITIES AND UTILITY SERVICES

    CHAPTER 9 ELECTRIC SERVICESPART 568 INTERCONNECTION OF GENERATING FACILITIES WITH A RATED CAPACITY UP TO AND INCLUDING 10 M

    CONNECTING TO A UTILITY SYSTEM

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    12/31

    UL 1741

    UL 1741 (Second Edition, January 28, 2010)incorporates:

    IEEE 1547 Standard for Interconnecting Distributed Resour

    with Electric Power Systems

    IEEE 1547.1 Standard for Conformance Testing ProceduresEquipment Interconnecting Distributed Resources.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    13/31

    UL 1741

    UL 1741 (2nd Edition) also includes requirements f

    Construction, materials, wiring, component spacing, etc.

    Protection against risks of injury against persons

    Output characteristics and utility compatibility (includes IEEE1547)

    Rating, Marking

    Specific Tests for various technologies (PV, Wind, MicroturbinFuel Cell Engine, etc.)

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    14/31

    UL 1741

    The CCW regenerative Enersaver Power II habeen tested and certified compliant with therequirements of the stringent UL 1741 standar(2nd Edition).

    This testing has certified the Enersaver Powermeets the standards for alternative energy,

    distributed and grid parallel generation system

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    15/31

    UL 1741

    The Enersaver Power II is the first, and currenthe only drive system which complies with thisimportant standard.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    16/31

    UL 1741 Key Requirements

    Harmonic Distortion of less than 5% I-THD

    The measured total harmonic distortion of the currentoutput from inverters must be below 5%.

    The power coming on to the grid is expected to be cleaand not interfere with the operation of the electricsystem.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    17/31

    UL 1741 Key Requirements

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    18/31

    THD taken with Enersaver -VFD running at 60HZ, snap shot

    represents a 20 minute capture.

    This is 4.5% THD for Current .. 0.8% THD for Voltage

    Oilfield Power2

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    19/31

    UL 1741 Key Requirements

    Anti-Islanding Verification Test

    This standard ensures that the inverter will properly shdown during a power interruption and isolate itself from

    the electric grid.

    This standard is of utmost importance to electricdistribution companies as it relates to safety for theirworkers.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    20/31

    UL 1741 Key Requirements

    Frequency variation test

    The inverter must pass a series of simulated tests toadjust to the frequency of the grid AC power within

    specified time standards.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    21/31

    UL 1741 Key Requirements

    Line/Grid Synchronization Tests

    The inverter system must be able to automaticallysynchronize to the grid under many different condition

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    22/31

    UL 1741 Key Requirements

    Dielectric Voltage Withstand Test

    The inverter must be able to withstand 1,000 volts plustwice the rated voltage of the inverter between the inp

    stage and ground, the output stage and ground, andbetween the input and output stages.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    23/31

    UL 1741 Key Requirements

    Other Tests Performed for UL 1741Compliance: Voltage Variation Output Test

    Component Short Circuit Test

    Loss of Control Circuit Test

    Temperature Withstand Test

    Line/Grid Interactive Test

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    24/31

    UL 1741 Key Requirements

    Other Tests Performed for UL 1741Compliance: Voltage Variation Output Test

    Component Short Circuit Test

    Loss of Control Circuit Test

    Temperature Withstand Test

    Line/Grid Interactive Test

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    25/31

    UL 1741

    The Enersaver Power II is the first, and currenthe only drive system which complies with thisimportant standard.

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    26/31

    Benefits of UL 1741Compliant Oilfield Drive Systems

    Regenerate Electricity

    for Sale back onto Electric Grid

    Reduce own consumption

    Reduction of energy consumed

    Reduction of demand charges

    Oilfi ld E

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    27/31

    Oilfield Enersaver

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    28/31

    Benefits of UL 1741Compliant Oilfield Drive Systems

    Reactive Power (KVARs) go from consuming tgenerating

    Generating KVARs:

    Decreases current/amperage required for motor wo

    Reduces or eliminates voltage sags

    Significantly decreases KVA demand charges

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    29/31

    Benefits of UL 1741Compliant Oilfield Drive Systems

    Clean Utility Grade power generated

    Returned to grid for $$ credit

    Benefits other electric devices in area

    active Power (KVARs) go from consuming togenerating

    GREEN Carbon Offsetting Power

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    30/31

    Benefits of UL 1741Compliant Oilfield Drive Systems

    Increased safety of workers and public

    Opportunities to participate in demandreduction/demand response programs

    Provides greater energy efficiency

  • 7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02

    31/31

    Benefits of UL 1741Compliant Oilfield Drive Systems

    QUESTIONS?