Presentation to Artificial Lift ForumNovember 2011
UL 1741 Distributed Generation Standard
Ronald A. Dombrowski,
Vice President, CCW
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
2/31
What is UL1741 and why should I care?
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
3/31
UL 1741 is the standard that inverter-basedgenerators must meet to put electricity on the
grid
and get paid for it.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
4/31
You should care about UL1741 because up to40% of the energy you are putting into yourbeam pumps may be recovered with aregenerative drive system.
With a UL 1741 certified system, that can comright off your electric bill.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
5/31
You should care about UL1741 because up to40% of the energy you are putting into yourbeam pumps may be recovered with aregenerative drive system.
With a UL 1741 certified system, that can comright off your electric bill.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
6/31
Distributed Generation in TEXAS
Distributed Generation:An electrical generating facility located at acustomer's point of delivery (point of commoncoupling) of ten megawatts (MW) or less and
connected at a voltage less than 60 kilovolts (kVwhich may be connected in parallel operation tothe utility system.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
7/31
Distributed Generation in TEXAS (cont)
The Public Utility Commission of Texas (PUCTencourages the use of distributed resources.
Texas Public Utility Regulatory Act (PURA) of1999 includes customer rights and safeguards
Section 39.101(b)(3) of PURA states A
customer is entitled to have access . . . to on-sdistributed generation . . .
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
8/31
Distributed Generation in TEXAS (cont)
The PUCT established Substantive Rules forinterconnecting distributed generation.
Substantive Rules Sections 25.211 and 25.212 addres Technical Aspects
Procedural Aspects
for interconnection of distributed generation.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
9/31
Distributed Generation in TEXAS (cont)
The PUCT established Safety Requirements forinterconnecting distributed generation.
Safety Requirements ensure DG is designed and
installed in a way that: is not a safety hazard to utility personnel, equipment or other
customers
Does not disturb other customers or degrade quality ofdistribution system
Provides reliable service to DG owner and utility
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
10/31
Distributed Generation in TEXAS (cont)
UL 1741 forms a part of the Safety Requirements
Virtually all Texas utilities require compliance with UL
1741 standards
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
11/31
Distributed Generation in NEW MEXICO
17.9.568.8 APPLICABLE CODES AND STANDARDS:B. In order to qualify for any interconnection procedur
each generating facility generator shall be inconformance with the following codes and standard
as applicable:(3) UL 1741 Inverters, converters and controllers for u
in independent power systems or equivalent.
TITLE 17 PUBLIC UTILITIES AND UTILITY SERVICES
CHAPTER 9 ELECTRIC SERVICESPART 568 INTERCONNECTION OF GENERATING FACILITIES WITH A RATED CAPACITY UP TO AND INCLUDING 10 M
CONNECTING TO A UTILITY SYSTEM
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
12/31
UL 1741
UL 1741 (Second Edition, January 28, 2010)incorporates:
IEEE 1547 Standard for Interconnecting Distributed Resour
with Electric Power Systems
IEEE 1547.1 Standard for Conformance Testing ProceduresEquipment Interconnecting Distributed Resources.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
13/31
UL 1741
UL 1741 (2nd Edition) also includes requirements f
Construction, materials, wiring, component spacing, etc.
Protection against risks of injury against persons
Output characteristics and utility compatibility (includes IEEE1547)
Rating, Marking
Specific Tests for various technologies (PV, Wind, MicroturbinFuel Cell Engine, etc.)
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
14/31
UL 1741
The CCW regenerative Enersaver Power II habeen tested and certified compliant with therequirements of the stringent UL 1741 standar(2nd Edition).
This testing has certified the Enersaver Powermeets the standards for alternative energy,
distributed and grid parallel generation system
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
15/31
UL 1741
The Enersaver Power II is the first, and currenthe only drive system which complies with thisimportant standard.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
16/31
UL 1741 Key Requirements
Harmonic Distortion of less than 5% I-THD
The measured total harmonic distortion of the currentoutput from inverters must be below 5%.
The power coming on to the grid is expected to be cleaand not interfere with the operation of the electricsystem.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
17/31
UL 1741 Key Requirements
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
18/31
THD taken with Enersaver -VFD running at 60HZ, snap shot
represents a 20 minute capture.
This is 4.5% THD for Current .. 0.8% THD for Voltage
Oilfield Power2
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
19/31
UL 1741 Key Requirements
Anti-Islanding Verification Test
This standard ensures that the inverter will properly shdown during a power interruption and isolate itself from
the electric grid.
This standard is of utmost importance to electricdistribution companies as it relates to safety for theirworkers.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
20/31
UL 1741 Key Requirements
Frequency variation test
The inverter must pass a series of simulated tests toadjust to the frequency of the grid AC power within
specified time standards.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
21/31
UL 1741 Key Requirements
Line/Grid Synchronization Tests
The inverter system must be able to automaticallysynchronize to the grid under many different condition
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
22/31
UL 1741 Key Requirements
Dielectric Voltage Withstand Test
The inverter must be able to withstand 1,000 volts plustwice the rated voltage of the inverter between the inp
stage and ground, the output stage and ground, andbetween the input and output stages.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
23/31
UL 1741 Key Requirements
Other Tests Performed for UL 1741Compliance: Voltage Variation Output Test
Component Short Circuit Test
Loss of Control Circuit Test
Temperature Withstand Test
Line/Grid Interactive Test
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
24/31
UL 1741 Key Requirements
Other Tests Performed for UL 1741Compliance: Voltage Variation Output Test
Component Short Circuit Test
Loss of Control Circuit Test
Temperature Withstand Test
Line/Grid Interactive Test
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
25/31
UL 1741
The Enersaver Power II is the first, and currenthe only drive system which complies with thisimportant standard.
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
26/31
Benefits of UL 1741Compliant Oilfield Drive Systems
Regenerate Electricity
for Sale back onto Electric Grid
Reduce own consumption
Reduction of energy consumed
Reduction of demand charges
Oilfi ld E
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
27/31
Oilfield Enersaver
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
28/31
Benefits of UL 1741Compliant Oilfield Drive Systems
Reactive Power (KVARs) go from consuming tgenerating
Generating KVARs:
Decreases current/amperage required for motor wo
Reduces or eliminates voltage sags
Significantly decreases KVA demand charges
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
29/31
Benefits of UL 1741Compliant Oilfield Drive Systems
Clean Utility Grade power generated
Returned to grid for $$ credit
Benefits other electric devices in area
active Power (KVARs) go from consuming togenerating
GREEN Carbon Offsetting Power
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
30/31
Benefits of UL 1741Compliant Oilfield Drive Systems
Increased safety of workers and public
Opportunities to participate in demandreduction/demand response programs
Provides greater energy efficiency
7/28/2019 Artificialliftforum Ul1741presentation Final 120215145546 Phpapp02
31/31
Benefits of UL 1741Compliant Oilfield Drive Systems
QUESTIONS?