Friday January 27th, 2012 Comcast Boot Road Data Center
Agenda
• 8:30-9:00 Breakfast and networking
• 9:00-9:15 Welcome» Logistics» Introductions» Topics for Discussion
• 9:15-10:30 Session One:
– New Year, New objectives and priorities… – Vendor Spotlight:
» Peter Panfil, Emerson Network Power VP Global Power Sales• Current trends and future challenges
• 10:30-10:40 Break
• 10:40-11:30 Data Center Tour
• 11:30-12:00 Session Two:
– User Spotlight: Donna Manley – Post mortem procedures
• 12:00-1:00 Lunch
2012 Goals• Expansion of data centers• Audit with RFID• Bussway
Vendor Spotlight:
Peter A. Panfil VP Global Power Sales
Emerson Network Power
The State of the Data Center:Current trends and future challenges
AC Power Technology AC Power Technology
DVL DCUG
Jan 2012
Page 6COMPANY CONFIDENTIAL
AgendaAgenda Top data center challenges
Distributed (1+N) and central (N+1) static switch
Transformer based and transformer free UPS
Static switches improve MTBF in distribution
Distribution voltage trends and considerations
Page 7COMPANY CONFIDENTIAL
Infrastructure Management
Heat Density
Availability
Energy Efficiency
Power Density
Top Data Center Challenges Top Data Center Challenges
Source: Data Center Users’ Group Survey
Virtualization,Cloud
Increasing Demand
Reduced Budget
Higher Density
Regulation Compliance
IT Outsourcing Consolidation
Efficiency & Green
initiatives
External forces
changing the business climate
Business & technology
forces pressing on the data
center
Facility Challenges
7
Page 8COMPANY CONFIDENTIAL
Top Data Center Manager ConcernsTop Data Center Manager ConcernsRank Spring 2005 Fall 2007 Spring 2008 Spring 2009 Fall 2009 Spring 2010 Spring 2011
1Heat Density
78%Heat Density
64%Heat Density
56%Heat Density
55%Availability
56%
Monitoring Infrastructure
Mgt51%
Availability53%
2Power Density
64%
Power Density
55%
Power Density
50%
Energy Efficiency
47%
Monitoring Infrastructure
Mgt49%
Heat Density49%
Monitoring Infrastructure
Mgt52%
3Availability
57%
Energy Efficiency
39%
Availability45%
Monitoring Infrastructure
Mgt46%
Heat Density46%
Availability47%
Heat Density47%
4Space
Constraints32%
Availability33%
Monitoring Infrastructure
Mgt43%
Availability41%
Energy Efficiency
40%
Energy Efficiency
44%
Energy Efficiency
44%
5Change
Management28%
Space Constraints
29%
Energy Efficiency
40%
Power Density
35%
Power Density
25%
Power Density
36%
Power Density
29%
6
Monitoring Infrastructure
Mgt18%
Monitoring Infrastructure
Mgt27%
Space Constraints
26%
Space Constraints
29%
Space Constraints
25%
Space Constraints
21%
Space Constraints
18%
Monitoring / Infrastructure Management properly balances the needs of efficiency and availability
Data Center Users’ Group Survey
Page 9COMPANY CONFIDENTIAL
Trend Liebert Solution
Energy Efficienc
y
High-Efficiency Products
Liebert APMLiebert NXLiebert NXL
Features Improving Efficiency
Softscale Intelligent Eco ModesTP1 (Energy Star) Rated Distribution TransformersDistribution Voltages (240/139 and 415/240V)
Services Data Center Power & Cooling Assessments
Increased Density
Increasing Power Requirements
2 Stage (Segmented) Distribution400A Panel Boards w/ 100% Rated MainsBusway SolutionsMPX – up to 60A Rack PDU575V NXL
System Focus
Partnerships & Marketing Materials
Universal Switchgear ProgramLarge Systems Design Guide
High Availability Topologies
Development of 1+N for Large SystemsModular Systems with Internal Redundancy
Renewable Energy
Existing Products Flywheel Systems
New Products
Alternative Energy StorageSolar – ENPC: Solar Controller, EP: Solar
Inverter; DOE Funded Smart Grid ResearchWind – ENPC: Wind Converter
Liebert AC PowerTrends and Strategies
Page 10COMPANY CONFIDENTIAL
Dual Corded Dual BusRequires custom switchgear for power tie
Maximum Loading N/2For 4x1000 kVA=2000 kVA Max Load
UPS 1 UPS 2
PDU PDU
STS STS
UPS 3 UPS 4
PDU PDU
STS STS
Interleaved Dual BusDoes not require complex switchgear
STS does the power tieMaximum Loading N/2
For 4x1000 kVA=2000 kVA Max Load
UPS 1 UPS 2 UPS 3 UPS 4
PDU PDU PDU PDU
STS STS STS STS
UPS 1 UPS 2 UPS 3 Reserve
STS STS STS
PDU PDU PDU
Reserve/Catcher Dual BusDoes not require complex switchgear
STS does the power tieMaximum Loading N-R
For 4x1000 kVA=3000 kVA Max Load
50% Utilization
75% Utilization
50% Utilization
66% Utilization
Ring Dual Bus (Distributed Reserve)Does not require complex switchgear
STS does the power tieMaximum Loading (N-1)/N
For 4x1000 kVA=3000 kVA Max Load
STS STSSTS STSSTSSTS
UPS 1 UPS 3
PDU PDUPDU PDUPDUPDU
UPS 2
High Availability ConfigurationsHigh Availability Configurations
Page 11COMPANY CONFIDENTIAL
UPSCore
SS SS SS
Paralleling Cabinet
UPSCore
UPSCore
IT Load
UPSCore STS
System Control Cabinet
UPSCore
UPS Core
IT Load
Distributed Bypass (1+N)
Distributed static switches
Individual modules manage load transfers
Cannot parallel different sized UPS
Central Bypass (N+1)
Centralized static transfer switch
System-level control, fault tolerant
Size of STS determines total capacity
Options for parallel redundant UPSOptions for parallel redundant UPS
Page 12COMPANY CONFIDENTIAL
N+1 vs 1+NN+1 vs 1+N For a system of 4x750kVA
– 1+N will cost $1.2M , max aic 100kaic– N+1 will cost $1.4M , max aic 200kaic– If specifications allow both the 1+N will always be cheaper
When operating on inverter both have identical performance– N+1 has better fault transfer to bypass due to one 3000/4000amp breaker– 1+N has more sag due to parallel SS/inductors/1200a CB during fault transfer.– Since MTBF of NXL module is 200,000 hours the 4 module system will transfer to
bypass every 50,000 hr or 6 years if capacity and statistically never if redundant
1+N since it is composed of SMS can easily be split and sent to different locations– Requires two upstream feeder breakers or single input kit versus one for N+1
NEC70E requires both to have downstream ROB to be able to service one module while system is energized
Page 13COMPANY CONFIDENTIAL
Transformer Based UPS System Single Module, Topology Three-LineTransformer Based UPS System Single Module, Topology Three-Line
MIB
OutputMBB
3P
CB2
BFB
E
BIB
EG
FBO
AC
FBO
AC
GEC
MBJ
N N
EG
A
Trap Disconnect
CB1
12P isolated
12P non isolated
or
To Batteries
Negative DC bus
Positive DC bus
Output -AC
+
+
+
+
+
+
Battery and DC Bus
Isolation
Input Isolation
Output Isolation
Neutral-Gnd Management;Low Common Mode Noise;
Separately Derived Source
Bypass can be connected to separate utility source
Page 14COMPANY CONFIDENTIAL
Transformer Less UPS System Single Module, Topology Three-LineTransformer Less UPS System Single Module, Topology Three-Line
No Input Isolation
Additional DC Converter
Less Eff Rectifier
High DC Bus
Neutral Mgt / Control Required
Some topologies require the bypass to be connected to
the same utility source
No Output Isolation
Page 15COMPANY CONFIDENTIAL
Application PhilosophyTransformer Based & Transformer Free UPSApplication PhilosophyTransformer Based & Transformer Free UPS There are appropriate applications for both transformer
based and transformer free UPS– Many customers have multiple applications with different priorities
Transformer based enterprise UPS’s offer the highest availability – Galvanic isolation is provided for DC fault protection– Output isolation protects the critical load and simplifies fault
management– Use ultra-reliable, efficient SCR-based rectifiers and simple lower
voltage inverters– Can feed rectifier and bypass from dual Separately Derived Sources– Inherently compatible with High Resistance Grounded systems
Transformer-free UPS’s offer low TCO with high availability– Double conversion efficiency up to 96% – Uniformly Low input harmonics with consistent high power factor.– Power distribution provides complete solution for transformer free UPS
Page 16COMPANY CONFIDENTIAL
Characteristic Transformer Free
Transformer Based
AC-AC Double Conversion Efficiency
96% Range 94% Range
Eco Mode Efficiency Up to 99% Up to 99%
Ground Fault Protection Coordination
External or Incremental
Inherent
Arc Flash Mitigation External or Incremental
Inherent
> 480 volt ratings for high power density
Additional External Xformers Required
No Additional External Xformers Needed
Reduction in Common mode noise and EMI
No Yes
Rectifier Resiliency IGBT vs. SCR
Lower Higher
High Resistance Ground Compatibility
No Yes
Transformer Based –vs-Transformer Free Design
Transformer Based –vs-Transformer Free Design
Page 17COMPANY CONFIDENTIAL
Tier 3-4 UPS Power configuration into a Dual Input IT Load
MTBF UPS Out = UPS 1 = UPS2 Primary AC Input MTBF = S10 UPS MTBF out = > 1.6M hr MTBF Field ObservedBypass AC Input =
100 Hr MTBF
Bypass AC Input PDU MTBF > 9 M hrUPS 1 Field-Observed
Primary AC Input SMS MTBF > 1.7 M hr PDU
IT each AC Input MTBF =Simplified - Components in series
= 1/((1/MTBF UPS) + (1/MTBF PDU)) IT LoadMTBF = 1.4 M hr
Primary AC Input PDUUPS 2
Bypass AC Input SMS
System MTBFWithout Static SwitchesSystem MTBFWithout Static Switches
Module Demonstrated MTBF Block Diagram
Page 18COMPANY CONFIDENTIAL
Tier 3-4 UPS Power configuration with STS 2 into a Dual Input IT Load
MTBF UPS Out = UPS 1 = UPS2 Primary AC Input MTBF = S10 UPS MTBF out = > 1.6M hr MTBF Field ObservedBypass AC Input =
100 Hr MTBF
Bypass AC Input STS MTBF > 7.2 M hr PDU MTBF > 9 M hrUPS 1 MTBF > 1.7 M hr Field-Observed
Primary AC Input SMS STS2 PDU
enter
UPS MTBF = 1.7Combined MTBF of two STS 2 Field-Observed MTBF:Paralleled UPS outputs Field-observed STS MTFB output
= MTBF1+MTBF2+((MTBF1*MTBF2)/(MTTR)) ≈ 7.2 M hr MTBF IT LoadMTBF = 113,441 M hr IT each AC Input MTBF =
Simplified - Components in series where Mean Time to Repair [MTTR] = 24 hrs = 1/((1/Para UPS Out) + 1/MTBF STS) + (1/MTBF PDU)) where UPS repair is less than 8 hrs enter MTBF = 4.0 M hr
Primary AC Input STS2 PDUUPS 2
Bypass AC Input SMS
System MTBF Improvement With Static SwitchesSystem MTBF Improvement With Static Switches
Module Demonstrated MTBF Block Diagram
Page 19COMPANY CONFIDENTIAL
STS2
Multiple Rows
Service Feed
Surge Suppression
Engine Generators
Generator Paralleling Switchgear
Feed to UPS
Input Switchgear
Precision Cooling
LBS
RDC/FDC
RDC/FDC
Racks
UPS A
UPS B
Alte
rna
te
Prim
ary
Prim
ary
Alte
rna
te PDU: PPC/FPC
PDU: PPC/FPC
STS2
Dual Bus = twice as many power cables
Traditional Dual Bus, 2NTraditional Dual Bus, 2N
Page 20COMPANY CONFIDENTIAL
480VAC • RDC• UPS • Rack480/277V 480/277V
480VAC • RDC• UPS • Rack415/240V 415/240V
480VAC • UPS • PDU • Rack480V 208/120V
600VAC • UPS • PDU • Rack600V 415V
600VAC • UPS • PDU • Rack600V 208/120V
415VAC • RDC• UPS • Rack415/240V 415/240V
Tod
ay
Em
erg
ing
Efficiency improvement ???
Distribution VoltagesDistribution Voltages
Page 21COMPANY CONFIDENTIAL
Isolation Transformers At The PDUIsolation Transformers At The PDUPROS Single point ground, separately derived source with
safety ground closer to the load reduces susceptibility to lightning and other transients
Only requires a 3 wire system to the PDU input Provide impedance which reduces available fault currents
~ and Arc Flash potential at distribution points
CONS Size – PDU’s with transformers can be larger Transformation losses …However…today’s TP-1
transformers are typically 98.5% + efficient Higher weight and cost
Page 22COMPANY CONFIDENTIAL
PDU Transformer Efficiency
PDU Transformer Efficiency
96.00
96.50
97.00
97.50
98.00
98.50
99.00
15% 25% 35% 50% 65% 75% 100%
% LOAD
% E
FF
ICIE
NC
Y
300 kVA K20
300 kVA STD
300 kVA K20 TP1
300 kVA STD TP1
$$$
Page 23COMPANY CONFIDENTIAL
A Fresh Look at the 400-415v SystemA Fresh Look at the 400-415v System Modern Power supplies are wide ranging 208v to 240v test
– Higher voltage equates to higher efficiency – about 0.3% gain Line to neutral connection – 230/400 or 240/415v
– Can be transformer free saving energy-1-3% gain, plus cooling savings– Fault current HAS been a major concern if transformer free
• 480 or 600v to 240/415 v with Auto (efficiency) or Iso. (aic and N-G) • Historically, vendors supplied pieces and parts, but not an end-to-
end solution for 400-415V in North America.– Neutral fault path and neutral noise are concerns with transformer free– No Rack PRU balancing issue
Line to Line connection – 120/208 and 127/240v– New copper TP-1 Transformers have 1.5% losses– Fault current is controlled by the transformer
• Panels, breakers, power cords, rack PDU and servers rated for fault current (aic) are readily available
– Neutral fault path and neutral noise are from server to isolation transformer only
Page 24COMPANY CONFIDENTIAL
Short Circuit Considerations (Historical)Short Circuit Considerations (Historical)Panelboards 208/120 & 240/139 Volt Panels
Rated at 250V
– Type NQ
– Available to 22kAIC
480/277 & 415/240 Requires Panels Rated to 600V
– Type NF
– Series rated with main CB at• 35,65 and 100kaic
– Physically larger
– More costly (10-25%)
Are your Rack PDUs and servers rated for this high AIC?
Page 25COMPANY CONFIDENTIAL
Fault CurrentArc Flash ConsiderationsFault CurrentArc Flash Considerations Arc flash?
– Bolted vs. arcing faults
– Significant incident energy released during the arcing event and is considered the “arc flash hazard”
NFPA 70E-2004 “A flash hazard analysis be done in order to protect personnel from the possibility of being injured by an arc flash”
Determination of required PPE - Personal Protective Equipment
Calculation of incidence of energy
– Ampere rating of over current protective device
– Operating time of the device
– Available fault current is key!!!
Page 26COMPANY CONFIDENTIAL
Solving the 415V AIC IssueSolving the 415V AIC Issue
PDU
UPSSYSTEM
3250 kVA34.5 kV – 480/277Z >= 5.32%
Isc ~ 73,480A
Isc ~ 17,576 A
300 kVA480V – 208/120VZ >= 4%
X
X
208 Volt Distribution
PDU
UPSSYSTEM
3250 kVA34.5 kV – 415/240Z >= 5.32%
Isc ~ 84,989A
Isc ~ 56,144 A
X
X
415 Volt Distribution
RACKIsc < 5kA
RACKIsc ~ 10-12kA
Problem• AC Distribution panels
• Lighting panels• Exposed buss (arch flash)• AIC of UL approved “touch
safe”• Rack PDUs
• AIC may exceed safe design
Solutions• Introduce impedance such as inductor or transformer
• Disadvantage efficiency• Advantage grounding and
fault management (tx)• I-Line Panels offer higher AIC (100k) and safer design• Higher AIC capable RPDU’s
Page 27COMPANY CONFIDENTIAL
Maximize your investment in breakers and gear with higher UPS System voltages
The higher the chosen voltage - the greater the potential capacity – 15% to 25%
5000 Amp System UPS System Voltage
415V 480V 600V
Max. Bus Capacity 3590 kVA 4152 kVA 5190 kVA
Distribution Voltage ConsiderationsUPS System Voltage and Capacity Distribution Voltage ConsiderationsUPS System Voltage and Capacity
Page 28COMPANY CONFIDENTIAL
Distribution Voltage Pros & ConsDistribution Voltage Pros & ConsPROS CONS
480 – 208/120
600 – 208/120
Most commonly accepted application Reduced aic – fault curent Uses standard 240V panelboard & breakers N-G bond at PDU
2-3% transformation energy loss 208V requires 2 pole breaker Reduces the number of poles
480 – 400/230
600 – 400/230
N-G bond at PDU( iso) Higher energy efficiency Higher energy density Higher UPS capacity - kVA Reduced AIC – fault current
0.5 to 1.3%% transformer energy loss Can’t power 120V equipment More circuits due to1-pole N-G bond (auto) at service entrance
480 – 480
480 – 480/277
No transformation energy losses No neutral required (unless 277V loads)
Can’t power 120V or 240V equipment Requires 480V panelboard & breakers Few servers at 480V & 277V Higher AIC – fault current at load
480 – 415/240
No transformation energy losses 240V load requires 1 pole breaker More useable pole spaces Higher energy efficiency
N-G bond at bypass transformer Requires 480V panelboard& breakers Requires UPS Maint Bypass Xfmr Higher AIC – fault current at load
415 – 415/240
No transformation energy losses Reduced cooling load 240V load requires 1 pole breaker More useable pole spaces Higher energy efficiency Save cost and weight of transformers in
PDUs
Can’t power 120V equipment Requires 480V panelboard& breakers Needs different approach to fault
current management N-G bond at service entrance Increase cost of full neutral and higher
ampacity – lower system kVA
Page 29COMPANY CONFIDENTIAL 29
29
Page 30COMPANY CONFIDENTIAL
Product Operating Hours Mod. MTBF Sys. MTBF
(Cur # Units) Oct 00 – Mar 11 Code 14 Code 15
Unfiltered Filtered
STS 2 (4,082) 121,462,656 Hrs. 886,589 Hrs. 8,675,904 Hrs.
S610 (6,642) 419,488,584 Hrs. 47,838 Hrs. 1,712,198 Hrs.
NXb (2,843)105,092,280 Hrs. 202,490 Hrs. 2,563,226 Hrs.
PPC (10,474) 878,674,536 Hrs. 2,670,743 Hrs. 10,217,146 Hrs.
FPC (1,951) 41,363,976 Hrs. 10,340,994 Hrs. 13,787,992 Hrs.
NXL (612) 5,581,704 Hrs. 206,730 Hrs. 1,395,426 Hrs.*
APM (113) 384,432 Hrs. 384,432 Hrs. 384,432 Hrs.
Liebert STS2, S610, NXb, PPC, FPC,NXL Reliability Summary May 2011Liebert STS2, S610, NXb, PPC, FPC,NXL Reliability Summary May 2011
Transfer To BypassCritical Bus Failure
* Updated Nov 2011 30
Page 31COMPANY CONFIDENTIAL
Power Business SegmentsPower Business Segments
Scale-OutCore Enterprise
Availability Capital/Operational Savings
Primary Technology
Transformer Based UPS
Transformer Based UPS in Eco-Mode
Transformer Free UPS
Transformer Free UPS in Eco-Mode
Battery on Server Model
Customer Type
Traditionalist Opportunist Experimentalist
Customer Behavior & Motivation
Firmly adheres to long-held, proven industry standards to
maximize infrastructure availability
Operates on the edge of acceptable operating
recommendations taking calculated risks to balance
financial costs and availability
Ventures outside of industry standards and best-practices with the goal to significantly
reduce financial costs
Customer Attributes
• Providing mission critical computing to customers
• Required uptime based on government regulations
• Extremely high cost of application downtime
• Providing less critical computing to internal or external customers
• Need to meet customer SLAs for uptime with limited penalties
• Balancing cost of downtime with OPEX
• Customers still expect application high availability
• Basic services are provided for limited fees with no guarantees
• High compute volume demands lowest computing costs possible
Critical Infrastructure
Primary Motivation
TCOAvailability Capital/Operational Savings
Page 32COMPANY CONFIDENTIAL
Dual Corded Dual BusRequires custom switchgear for power tie
Maximum Loading N/2For 4x1000 kVA=2000 kVA Max Load
UPS 1 UPS 2
PDU PDU
STS STS
UPS 3 UPS 4
PDU PDU
STS STS
Interleaved Dual BusDoes not require complex switchgear
STS does the power tieMaximum Loading N/2
For 4x1000 kVA=2000 kVA Max Load
UPS 1 UPS 2 UPS 3 UPS 4
PDU PDU PDU PDU
STS STS STS STS
UPS 1 UPS 2 UPS 3 Reserve
STS STS STS
PDU PDU PDU
Reserve/Catcher Dual BusDoes not require complex switchgear
STS does the power tieMaximum Loading N-R
For 4x1000 kVA=3000 kVA Max Load
50% Utilization
75% Utilization
50% Utilization
66% Utilization
Ring Dual Bus (Distributed Reserve)Does not require complex switchgear
STS does the power tieMaximum Loading (N-1)/N
For 4x1000 kVA=3000 kVA Max Load
STS STSSTS STSSTSSTS
UPS 1 UPS 3
PDU PDUPDU PDUPDUPDU
UPS 2
High Availability ConfigurationsHigh Availability Configurations
Break:See you in 15!
User Spotlight: Donna Manley
Post mortem procedures
Managing a Full Data Center Power Down
Donna M. Manley, MBAIT Senior Director, Computer Operations
University of Pennsylvania
July 3-4, 2009
36
July 3-4, 2009
37
January 2010 (Morning)
38
January 2010 (Noon)
39
40
41
Before you get started….
• Agree upon scope• Documentation • Validate infrastructure and architecture• Asset identification and application dependencies• Understand what pre-work can be completed• DR site and Vital Records storage providers on
standby• What’s the weather forecast?
Take the opportunity to do stuff you wouldn’t normally be able to without an outage!
42
43
44
45
Logistics….
• Coordination with Public Safety• Coordination with Facilities• Command Center• Know who will be there and when• Vendor Expectations• Accommodations, food, and beverage
46
47
48
Managing the Outage…
• Communication (Bridges, Web, Email)• Playbook• Change Freeze• Action Items to be remediated prior• Test plan• Points of Contact - Data Center/Facilities/Vendors• Who gives the “GO”
49
50
51
52
Post Outage…
• Communication (Bridges, Web, Email)• Execute Test Plan• Lessons Learned• Process and procedural modifications• Automation opportunities• Sleep!
Lots of great information was compiled for this event – keep it current!
53
Thank you for allowing me to share my thoughts with
you today!
Donna M. Manley, MBAIT Sr. Director, Computer OperationsITIL V3 Foundations CertifiedUniversity of [email protected]
Survey– Was this forum beneficial?– Was this the proper number of end users or
should the forum grow? If grow, please give a number you feel would be appropriate.
– How often should this forum meet? When?– What topics would you be interested in
discussing at the next meeting?– What other venues for this event would you like
to see?
Thank you for attending!