Mitigating Contamination Related Issues on T&D Equipment Lily Hoyer Simon Chan
PRESENTED BY SIMON CHAN T&D ASSET MANAGEMENT ENMAX POWER CORPERATION
PRESENTED TO
2012 APIC POWER AND ENERGY INNOVATION FORUM
INTRODUCTION
EFFECTS OF CONTAMINATION
MITIGATION METHODS
Introduction
Contamination has a significant impact on Enmax Power Corporation (EPC) Distribution Equipment and Material.
Contamination due to pollution, de-icers/road salt.
Effects of Contamination
Effects of contamination include: Flash Over on Equipment (Equipment failure)
Electrical Tracking (Wood Pins, Cross Arms) Pole Fires
Material Failures (Automatic Sleeves)
Consequences Poor reliability
Safety
$$$
4
Equipment/Material Flashover
Padmount Switchgear Rusting, peeling of paint on exterior.
Higher risk of flashovers
5
Electrical Tracking
Wood Pins
Androlite Arms
Wood Cross Arms
Insulators
6
Wood Pin
7
Androlite Arms
8
Pole Fires
Pole fires caused by contamination can only occur under the following conditions:
Leakage current from energized equipment must be passed through the wood pole to ground.
Localized leakage current densities must be increased to the point where sufficient heat is generated to begin pole fire process.
Road Salt vs Pole Fires
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
11
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
12
Androlite Conversion
Flattening Androlite Configuration to Current Construction Standards
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
14
Insulator Washing Maintenance Program
EPC initiated a multi-year insulator washing maintenance program acting on recommendations by the Canadian Electricity Association’s “The Prevention of Pole Fires” report.
Priority is on City of Calgary “Priority One” sanding routes.
Extra emphasis on areas where pole fires occurred previously.
Twice a year cycle. Late March to early April.
Late October to early September
Insulator Washing Maintenance Program
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
17
PMH Dry Ice Cleaning
Contaminants have caused flashovers to Pad Mount Switch Gear.
EPC has implemented a 5 year inspection and dry ice cleaning cycle for switches.
Currently, EPC is exploring possibilities of dry ice cleaning for Distribution Automation Pad Mounted Switches.
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
19
Material Standard Changes
Porcelian to Polymer Porcelain insulators Over insulated 34 kV polymer insulators.
Change to Porcelain Fused Cut Outs and lightning arrestors to Polymer.
Cross Arms (Wood to Fiber glass) Fiber glass replaces deteriorated wood crossarms.
Material Standard Changes
Material Standard Changes
Material Standard Changes
Cut Outs
23
Splices
24
Splices
Automatic to Compression Sleeves
Initial samples collected from the field were brought to a test lab and found significant corrosion from selected locations.
Corrosion was more evident near major roadways.
In 2011, only compression splices are to be used for all new construction and repair work.
Currently, EPC is collecting additional samples of automatic splices to a test lab for further analysis and will determine whether mechanical reinforcement or replacement with compression repair splices will be the next step.
25
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
26
Pole Fire Mitigation Program
In 2001, acting on the recommendation by CEA, “The Prevention of Pole Fires” report, EPC initiated a multi-year over-insulation and insulator washing maintenance program.
A total of $.57M were spent in the next seven years (2001 – 2007) at high pole fire re-occurrence areas to reduce pole fire incidences.
No structures that had been mitigated with upgraded insulation have been involved in pole fires.
Pole Fire Mitigation Program
The combination of weather as well as an increase of both the traffic and application of de-ice agent (i.e. road salt) has resulted in an increase in contamination of the distribution overhead structures.
In 2008, there were 76 pole fire incidents causing nearly 96000 customer interruptions and significant customer interruption time.
Pole Fire Mitigation Program
0
10
20
30
40
50
60
70
80
2001 2002 2003 2004 2005 2006 2007 2008 2009 2010 2011 2012(YTD)
Incid
en
ts
Year
Pole Fires
Pole Fire Mitigation Program
Alternatives Considered
1) Do nothing
2) Dry Ice Washing
3) Bonding
4) Over Insulation
Pole Fire Mitigation Program
Over Insulation
Wood crossarm Fiberglass crossarm
Porcelain insulator 34 kV class polymer insulator
Porcelain cutout Polymer cutout
Pole Fire Mitigation Program
Pole Fire Mitigation Program
Current Progress
Primarily focus is on mitigating overhead structures with equipment only.
Mitigated nearly 70% of these structures.
Expected completion 2014.
MITIGATION METHODS
Androlite Conversion
Insulator Washing
Switch Cleaning
Material Standard Change
Pole Fire Mitigation Program
Wood Pin Program
34
Wood Pin Program
Prevalent standard of insulator support until early 1970s when steel pins become industry standard.
Age and condition of the wood pins pose an increased risk to the safety of the general public and EPC employees.
Replacing to steel pins will minimize the hazards of line faults, pole-fires and line-down incidents associated with wood pin deterioration.
Wood Pin Program
Material Change
Wood pins to Steel Pins
Contamination due to road salt increased rate of deterioration in wood pins due to electrical tracking.
Wood Pin Replacement Project
Started in 2008
Nearly 4000 Structures containing wood pin to replace.
Expected completion in 2014.
Change this under "View" menu, Header/Footer options
enmax.com
Substation Insulator Pollution Contamination Management
PRESENTED BY LILY HOYER T&D ASSET MANAGEMENT ENMAX POWER CORPERATION
PRESENTED TO
2012 APIC POWER AND ENERGY INNOVATION FORUM
INTRODUCTION: Insulator Contamination?
ENMAX INSULATOR FLASHOVER STATISTICS
MITIGATION MANAGEMENT
PILOT PROJECT
LEARNINGS & CONCLUSION
INTRODUCTION OF INSULATOR CONTAMINATION
Insulator: isolation from the energized high voltage bus to ground.
Insulator contamination
41
INTRODUCTION OF INSULATOR CONTAMINATION
Insulator flashover: surface discharge when moisture condenses on solid insulation subject to particulate pollution
Factors of insulator flashover: Moisture condensation
Typical sources of insulator pollution depending on location
Coastal areas: salt from the sea
Industrial areas: fly-ash, variety of dust
Agricultural areas: soil dust, fertilizers, sugar cane production
Highways: salt from roads during winter time
SURFACE CORONA VEDIO AT 31S - 138KV bus trip Mar17-06
42
DAMAGED INSULATOR
43
INSULATOR FLASHOVER – CIRCUIT BRAKER FAILURE
44
OUR EXPERIENCE – INSULATOR FLASHOVER STATISTICS
YEARS OUTAGE NUMBERS
Prior 2001 3
2002-2006 3
2007 6
2008 2
2009 3
2010 3
2011 2
2012 0
45
2007 with a lot of flashover outages
2008 with most interrupted customers and longest interruption
Result in bus outage
MITIGATION MANAGEMENT
Preventive maintenance Review and enhance our substation washing program
(Sub washing committee was formed in 2008)
Meets twice a year to review frequencies
Analyzes past year’s sub washing for effectiveness
Corrective maintenance Visual inspection
Anticipation of the contamination (weather condition change)
Pilot project on condition monitoring of insulator contamination in 2009, installed in Fall 2010
46
SUBSTATION WASHING PROGRAM IN DETAIL
Factors of determining sub washing frequency Location of the sub (near high way, industry, river, land elevation) Criticality of the sub (control center input) Area external to the sub (construction, type of roads and speed limit) Type of insulators (polymer, porcelain) Type of bus (H bus-water drainage, Insulator hats are installed Past history Management and Field input
47
H bus vs. Round bus
Insulator Hat
Types of Insulator
Porcelain – easiest to track across.
Porcelain silicone – buys time since salt tracking is hampered
Polymer – best for preventing flashovers due to salt and pollution
Substation washing types
High pressure washing – 800psi for porcelain; 500psi for silicon coated porcelain
Flood washing – 300psi
Hand washing
Corn blasting
51
High Pressure Washing
Pros • Quicker
• Cheaper
• Best performance
Cons • Contractor availability
• Must be above 5 degrees
• Pushes dirt around insulator and not necessarily cleans it
• Can not wash potheads
• Not applied to porcelain silicone
Flood washing
Pros
• Less over spray
• Cheap
• Can potheads
Cons
• Contractor
• May not get rid of tough contaminants
• Weather dependant
• Pushes dirt around insulator and not necessarily cleans it
• May not get under the skirts
Hand Washing
Pros • Any temperature
Cons • Very costly
• Extra crews
• Longer outage
• Monotonous – poorer job performed as time wears on
• Destroys the silicone on insulators
• Pushes dirty to seams on polymer
Corn Blasting
Pros
• Can do hot
Cons
• Only on lower voltage
• Very messy
• Clean up
• Expensive
• Destroys the silicone on insulators
• Destroy the ground grid
Field experience of hand washing
Hand wash not suitable on Polymer insulators or porcelain silicone:
Granular dust/dirt/road grim particles seemed to scratch the surface with minimum force;
Hand washing push the dust against the seam (hard to clean)
Scratches on porcelain silicone insulator by hand wash
Seam of polymer insulators introduced in manufacturing process
Field Recommendations
Polymer and silicone insulators should be flood washed only.
High pressure or hand wash can be done on porcelain insulators
Washing Interval Spring and Fall
When the temperature fluctuates around the freezing mark, the roads are usually salted
Heavy spring accumulations of snow
May require frequent washing
Outages for washing and maintenance
Less critical washing deferred to fall to ensure outages for more critical washing
Substation Wash Schedule
Based on the substation criticality and pollution contamination level
Ongoing review of the washing frequency
Washing Frequency Substations
2 per year 10
1 per year 10
1 per 2 years 4
1 per 3 years 11
1 per 4 years 1
PILOT PROJECT – DOBLE IPM
Initialized in 2009 to utilize condition monitoring of pollution severity
Doble IPM installed on one substation next to highway and river
PILOT PROJECT – DOBLE IPM @ 32sub
64
LOCATION OF THE CURRENT SENSOR
65
CURRENT SENSTOR MOUNTING LOCATION
66
IPM 6 Channels connection
67
STANDALONE INSULATOR
68
DOBLE IPM METHODOLOGY
69
DOBLE IPM METHODOLOGY
70
Evaluation of Pollution Level
71
DOBLE IPM INTERFACE
72
DOBLE IPM LEAKAGE CURRENT MEASUREMENT
73
32S READING
DOBLE IPM LEAKAGE CURRENT MEASUREMENT
74
I_peak plot
Doble IPM EXPERIENCE
CPU down for a couple of times in the first year
Lake of Doble support
Benchmark is not available (Doble benchmark?) Washing
No risk tolerance in insulator flashover
Data correlation between IPM measurement and other data source (i.e. swab)
75
Conclusions
Washing committee with concentrated effort: flashover outages drops and duration decreases
Explore other means of pollution monitoring
76