EPRI Program on High
Frequency Testing
2© 2015 Electric Power Research Institute, Inc. All rights reserved.
EPRI High Frequency Program
1. Background on High Frequency Issues
2. EPRI High Frequency Program Purpose
and Scope
3. Component Test Program
4. High Frequency Component Evaluation
Criteria
3© 2015 Electric Power Research Institute, Inc. All rights reserved.
Ground motion estimates for some nuclear plant sites are
showing significant high frequency energy content
High Frequency Program – Background
4© 2015 Electric Power Research Institute, Inc. All rights reserved.
Seismic High Frequency – Background
In the late 1980s
EPRI and LLNL Hazard Studies suggested ground motions
could have significant amounts of high-frequency content
– Evaluation guidance was developed focusing on limited
displacements in high frequency motions
In the 2000s
Improved seismic hazard models included increased high-
frequency motions, especially for hard rock sites
New plant licensing criteria in the U.S. used the seismic
hazard to determine the site-specific seismic demand, which
brought the high-frequency issue to the forefront
– Additional guidance was developed with recommendations for
evaluating high frequency motions within the design process
5© 2015 Electric Power Research Institute, Inc. All rights reserved.
Seismic High Frequency – Background
Plotted as spectral accelerations,
the high frequency motions are
significant.
Plotted as spectral displacements,
the high frequency motions are
not significant.
𝑆𝑑 = 𝑆𝑎
2𝜋𝑓 2
6© 2015 Electric Power Research Institute, Inc. All rights reserved.
Seismic High Frequency – Background
NRC issued GI-199 to examine the issue of increased
seismic hazards on operating plants
NRC Near Term Task Force recommendations for seismic
evaluations asked licensees to estimate their seismic
hazards and GMRS using current criteria for new
plants
– EPRI report 1025287 (the SPID),
provided screening and evaluation
guidance for responding to the NRC
request for information, including
guidance for the treatment of high
frequency exceedances
7© 2015 Electric Power Research Institute, Inc. All rights reserved.
Identify components potentially vulnerable to loss of function
due to high-frequency vibratory motion
– Develop capacity data using shake table tests for potentially high-
frequency sensitive components
– Use accelerations that are high enough to address anticipated high-
frequency in-structure and in-cabinet responses of various plants
Identify resolution strategies
for components that prove
to be sensitive to high-
frequency motions
High Frequency Program – Purpose
8© 2015 Electric Power Research Institute, Inc. All rights reserved.
High Frequency Program – Phase 1
Random Multi-
frequency
0
1
2
3
4
5
6
10 100
Spec
tral
Acc
eler
atio
n (
No
rmal
ized
)
Frequency, Hz
HF SB1
HF SB2
HF SB3
HF SB4
HF SB5
HF SB6
HF SAwb
1 2 3 4 5 6
RMF + sine
beats
Test a limited number of components using a variety of
test methods to determine the optimal test protocol
Sine sweeps
(16 Hz to 64
Hz)
9© 2015 Electric Power Research Institute, Inc. All rights reserved.
Sine Sweep – 7.5g Front/Back, ~18 Hz
10© 2015 Electric Power Research Institute, Inc. All rights reserved.
Sine Sweep – 7.5g Front/Back, ~30 Hz
11© 2015 Electric Power Research Institute, Inc. All rights reserved.
Phase 1 Conclusions and Insights (EPRI 3002000706)
The multi-frequency input motion was the best input motion for determining high-frequency sensitivity. The 20 to 40 Hz frequency range was the best range for determining high-frequency sensitivity.
– The 16 to 32 Hz range overlapped more than necessary with standard testing
– The 24 to 48 Hz range did not provide significantly different results but could leave a gap between standard testing and the high-frequency testing
High-frequency sensitivity of contact devices is model specific; therefore, specific component testing was required
12© 2015 Electric Power Research Institute, Inc. All rights reserved.
High Frequency Program – Phase 2
Test a broad range of components with a diverse set of
manufactures and model numbers representative of
components installed in plants
Test using increasing acceleration levels until the
component fails the test or shake table limits are reached
13© 2015 Electric Power Research Institute, Inc. All rights reserved.
Test Sample Distribution
Testing performed on 153 items
Results are documented in
EPRI Report 3002002997
14© 2015 Electric Power Research Institute, Inc. All rights reserved.
Sample Results – Contactors & Motor Starters
15© 2015 Electric Power Research Institute, Inc. All rights reserved.
Key Test Program Conclusions (EPRI 3002002997)
Most components are very rugged
in the high-frequency range,
passing the tests without contact
chatter or malfunction at shake
table limits
Components that showed contact
chatter at high-frequency
accelerations less than 10g were compared with
previous results from 4.5 Hz to 16 Hz frequency range
In all cases, the high-frequency capacity was equal to or
great than the low-frequency capacity
No unique high-frequency sensitivities were identified
16© 2015 Electric Power Research Institute, Inc. All rights reserved.
Test results suggest components do not have unique high
frequency vulnerabilities
Amplification of high frequency ground motions in
structures and in electrical cabinets is not well known
What options are there for improving the in-structure and
in-cabinet response spectra estimates?
High Frequency Evaluation Criteria
17© 2015 Electric Power Research Institute, Inc. All rights reserved.
Together…Shaping the Future of Electricity
18© 2015 Electric Power Research Institute, Inc. All rights reserved.
Backup Slides
19© 2015 Electric Power Research Institute, Inc. All rights reserved.
• Electro-mechanical relays
(e.g., control relays, time delay
relays, protective relays)
• Circuit breakers
(e.g., molded case and power
breakers – low and medium
voltage)
• Control switches
(e.g., benchboard, panel,
operator switches)
• Electro-mechanical contactors
(e.g., MCC starters)
• Process switches and switches
(e.g., pressure, temperature, flow,
limit/position)
• Auxiliary contacts
(e.g., subcomponents
of MCCBs, contactors / starters)
• Transfer switches
(e.g., low and medium voltage
switches with instrumentation)
• Potentiometers (without locking
devices, and subcomponents
of relays)
High Frequency Program – Scope
Component type list from SPID Table 3-3 (EPRI 1025287)
20© 2015 Electric Power Research Institute, Inc. All rights reserved.
Applicable EPRI Reports
NP-7498, Industry Approach to Severe Accident Policy Implementation, November 1991
EPRI 1015108, Program on Technology Innovation: The Effects of High-Frequency Ground Motion on Structures, Components, and Equipment in Nuclear Power Plants, June 2007
EPRI 1015109, Program on Technology Innovation: Seismic Screening of Components Sensitive to High-Frequency Vibratory Motions, October 2007
EPRI 1025287, Seismic Evaluation Guidance: Screening, Prioritization and Implementation Details (SPID) for the Resolution of Fukushima Near-Term Task Force Recommendation 2.1: Seismic, February 2013
EPRI 3002000706, High Frequency Program, Phase 1 Seismic Test Summary, September 2013
EPRI 3002002997, High Frequency Program, High Frequency Testing Summary, September 2014